I have two questions for a project I need some guidance on and would appreciate some help.
Firstly, We require an ESFR system for a warehouse, but there is the presence of 1.0m wide by 7m+ long radiant panels every 3-4m spacing and 2-3m below the ceiling.
What is the best method to place sprinklers within 150mm of a radiant panel due to the obstruction? It is currently unclear due to the proximity of radiated heat how best to provide sprinkler protection.
Has anyone encountered this problem before and what solution did you incorporate?
We can use a higher-temperature sprinkler head, but this may not be enough so would be great to hear some commentary.
Secondly, There is an area with an extra hazard sprinkler system using K160 sprinkler heads at approx 12m high, where there are again rectangular obstructions 1.0m in width by 4-5m in length, 2-3m below the ceiling.
I have been reading the obstruction rules for standard spray sprinklers again and again but it is still unclear to me how to deal with suspended obstructions.
For these continuous obstructions, it appears as long as it is less than 1.2m in width and more than 450mm below the sprinkler deflector, it should not require additional protection.
Again, it would be great to hear some feedback and sense check on this, and if i have interpreted this correctly.
Thanks.
I have two questions for a project I need some guidance on and would appreciate some help.
Firstly, We require an ESFR system for a warehouse, but there is the presence of 1.0m wide by 7m+ long radiant panels every 3-4m spacing and 2-3m below the ceiling.
What is the best method to place sprinklers within 150mm of a radiant panel due to the obstruction? It is currently unclear due to the proximity of radiated heat how best to provide sprinkler protection.
Has anyone encountered this problem before and what solution did you incorporate?
We can use a higher-temperature sprinkler head, but this may not be enough so would be great to hear some commentary.
Secondly, There is an area with an extra hazard sprinkler system using K160 sprinkler heads at approx 12m high, where there are again rectangular obstructions 1.0m in width by 4-5m in length, 2-3m below the ceiling.
I have been reading the obstruction rules for standard spray sprinklers again and again but it is still unclear to me how to deal with suspended obstructions.
For these continuous obstructions, it appears as long as it is less than 1.2m in width and more than 450mm below the sprinkler deflector, it should not require additional protection.
Again, it would be great to hear some feedback and sense check on this, and if i have interpreted this correctly.
Thanks.