Heldbaum
Civil/Environmental
- Jan 27, 2017
- 128
Hi folks,
has any of you ever done a stair opening roughly 9'x7' in exist. RC building just next to the column? It's a 20-story residential building, two ways 8" flat slab - column structure. The client wants to create a duplex. It's at 10th floor. The opening would have to be located a few inches from the column so it's the worst location. I am quite familiar with ACI requirements when it comes to opening's location but there is nothing about openings strengthening to make it work. I cannot run any steel beams from column to column underneath the slab..I was thinking about steel flat bars connected to the columns and closing the edge of the opening from 3 sides with reinf. welded to the side plate. Does anyone have any experience with something like that? Any good reference? I see two obvious issues:
1. Punching shear
2. Temporary slab shoring - it's a residential building so LL 40 psf, and the concrete slab is min. 8" so DL is more than twice bigger.
I already spoke about that with my more experienced colleagues but I would like to get some insight from you guys. Thanks!
has any of you ever done a stair opening roughly 9'x7' in exist. RC building just next to the column? It's a 20-story residential building, two ways 8" flat slab - column structure. The client wants to create a duplex. It's at 10th floor. The opening would have to be located a few inches from the column so it's the worst location. I am quite familiar with ACI requirements when it comes to opening's location but there is nothing about openings strengthening to make it work. I cannot run any steel beams from column to column underneath the slab..I was thinking about steel flat bars connected to the columns and closing the edge of the opening from 3 sides with reinf. welded to the side plate. Does anyone have any experience with something like that? Any good reference? I see two obvious issues:
1. Punching shear
2. Temporary slab shoring - it's a residential building so LL 40 psf, and the concrete slab is min. 8" so DL is more than twice bigger.
I already spoke about that with my more experienced colleagues but I would like to get some insight from you guys. Thanks!