mechfp

Mechanical
Dec 21, 2012
9
Hi All, M new to HVAC designing. Wanna know more about Stairwell Pressurization. Gone through many threads but need some basic explanation. Please provide some link or document.
 
Replies continue below

Recommended for you

Yessir, ElSid1. The AHJ may not make good sense but he (or she) is the law. Ick.

Best to you,

Goober Dave

Haven't see the forum policies? Do so now: Forum Policies
 
Too funny. Nice input DRWeig. Code requires .15-.35" stairwell pressure. Max door opening force by Life Safety code is 30#. I know from experience this limits stair pressure to about midway through the required .15-.35" range. You have to add normal force applied by the closer (security doors need to shut and latch consistently) during non-fire conditions. So if the California egress door force limit is 15 pounds, your calcs show that code stair pressure cannot be met during a fire situation.

So the solution would be to buy special doors or closers? Are the Code writers related to the manufacturers of these products?
 