Standard formular for IDMT Relay Curve 1
Darrick
5
Anyone know the required standard for IDMT Relay Curve? What is the Equation/Formular? Thanks.
Darrick, there are many many IDMT curves about. You need to ask yourself the question: which one do I want to use?
cheers Johnspark
I am referring to the 3/10 curve. I would like to check using manual calculation say for a required setting after reading off the graph.
By 3/10, I believe you are talking about the Normal Inverse (NI) curve. Formulas below:-
t = (k.B)/((I/Is)^a - 1)
where t = operating time (sec)
k = TMS (time multiplier settings)
I = measured current value (A)
Is= set current value
a B
Normally Inverse 0.02 0.14
Very Inverse 1.0 13.5
Extremely Inverse 2.0 80.0
Long Time Inverse 1.0 120.0
NI = 3/10, VI = 1.2/10, EI = 0.8/10, LTI = 12/10.
You can also refer to BS142.1966 or IEC 255-4.
Thank you so much for the information guys. Been really helpful.