Ahmedbadr87
Mechanical
- Jun 10, 2018
- 23
We are installing sprinkler system network in Hospital and I have couple of questions with regard to installing standard sidewall sprinklers
1.]We have standard sidewall sprinklers in the corridor , ( I attach a dwg ) ,
as per NFPA 13 2019
10.3.4.1.3 Where sidewall spray sprinklers are installed along the length of a single wall of
rooms or bays, they shall be spaced in accordance with the maximum spacing provisions of
Table 10.3.3.2.1.
IS this clause applicable only to rooms only also i can apply where HSW sprinklers installed on corridor?
2.In rooms we install mix of pendent sprinklers and HSW Sprinklers,
As per NFPA 13 2019
10.3.4.1.6 Sidewall spray sprinklers shall be permitted to be installed on opposing or adjacent
walls, provided no sprinkler is located within the maximum protection area of another
sprinkler.
IS this clause only applicable when two Sidewall sprinklers installed nearby each other or shall be also applied in my case where i have pendent and HSW in the same room?
1.]We have standard sidewall sprinklers in the corridor , ( I attach a dwg ) ,
as per NFPA 13 2019
10.3.4.1.3 Where sidewall spray sprinklers are installed along the length of a single wall of
rooms or bays, they shall be spaced in accordance with the maximum spacing provisions of
Table 10.3.3.2.1.
IS this clause applicable only to rooms only also i can apply where HSW sprinklers installed on corridor?
2.In rooms we install mix of pendent sprinklers and HSW Sprinklers,
As per NFPA 13 2019
10.3.4.1.6 Sidewall spray sprinklers shall be permitted to be installed on opposing or adjacent
walls, provided no sprinkler is located within the maximum protection area of another
sprinkler.
IS this clause only applicable when two Sidewall sprinklers installed nearby each other or shall be also applied in my case where i have pendent and HSW in the same room?