I have had a 3hp 3 phase motor running seasonally, intermittent (half hour runs separated by hours) for several years now driving a centrifugal pump. It is powered by a Phase o Matic or some such brand static "phase converter" which is essentially a start relay used to apply voltage (phase shifted by a capacitor) to the 3rd phase to the motor.
Used as directed, the converter manufacturer does not recommend loading the motor to more than 2/3 of it's rating. I cannot determine actual loading of the pump with the information available, but to go by the performance of the motor and the fact that it has survived in this service for more than a few years, it must be fairly lightly loaded.
I have had a run capacitor (25uF) between one wire of the single phase supply and the 3rd (synthesized)phase to the motor. This arrangement produces ~2 amps on that phase and ~9 amps and ~7 amps on the other two which are powered directly off the single phase supply. I can increase the run capacitance (50 uF)and get in the range of 6 amps on the synthesized phase, but the high amperage phase will rise to ~12 amps if I do that. All amperages measured by a clamp on digital meter.
Wye connected TEFC NEMA 145T motor, dual voltage running on 208-230 (2 parallel wye connection) supplied with ~245 volts single phase. Rated amps at 230V is ~7.6 amps and at 208V is 8.0 amps. Service factor 1.15
Am I better off with some amperage on the 3rd phase from the "run" capacitors being in the circuit, but causing an imbalance/high amperage in the other two phases, or would the motor be better off with no voltage on the 3rd phase and balanced/lower amps on the two single phase powered phases.
I know a VFD with single phase input would be just the ticket, but would like to optimize this arrangement.
Thanks!
Used as directed, the converter manufacturer does not recommend loading the motor to more than 2/3 of it's rating. I cannot determine actual loading of the pump with the information available, but to go by the performance of the motor and the fact that it has survived in this service for more than a few years, it must be fairly lightly loaded.
I have had a run capacitor (25uF) between one wire of the single phase supply and the 3rd (synthesized)phase to the motor. This arrangement produces ~2 amps on that phase and ~9 amps and ~7 amps on the other two which are powered directly off the single phase supply. I can increase the run capacitance (50 uF)and get in the range of 6 amps on the synthesized phase, but the high amperage phase will rise to ~12 amps if I do that. All amperages measured by a clamp on digital meter.
Wye connected TEFC NEMA 145T motor, dual voltage running on 208-230 (2 parallel wye connection) supplied with ~245 volts single phase. Rated amps at 230V is ~7.6 amps and at 208V is 8.0 amps. Service factor 1.15
Am I better off with some amperage on the 3rd phase from the "run" capacitors being in the circuit, but causing an imbalance/high amperage in the other two phases, or would the motor be better off with no voltage on the 3rd phase and balanced/lower amps on the two single phase powered phases.
I know a VFD with single phase input would be just the ticket, but would like to optimize this arrangement.