VAMechE
Mechanical
- Jan 20, 2008
- 8
I would like some clarification/advise/sanity check on a project I am reviewing at work. I was handed a project (already in construction) for a municipal water pumping system for one of our hospitals. I will describe the system first (starting at intake end) then ask my question.
The intake in the hudson river is a screened inlet (with about 1 ft of loss at the system design point of 150gpm) attached to long radius elbow and then ~1800' of 8" DR-11 HDPE pipe to the pump station on the banks of the river.
Mean low tide is about 15.5' below the centerline of the pump.
Where the line enters the pump house there is 2 8" x 4" Wye's (one feeds each redundant pump). a 4" gate valve, a 4" basket strainer, another 4" gate valve, then a 4"x3" concentric reducer on the inlet of the pumps.
The pumps are Goulds 3796 3x3-13 MTi's with a cut down impeller of 12.875". The pumps are in parallel and one will be in standby while the other is active. Design flow rate is 150gpm at a TDH of 140' The pump spec sheet lists and NPSHa of 10ft, a NPSHr or 4ft (at 150gpm, but the curve does not go below 150gpm). I found that on the goulds website they listed "static suction lift" at 20ft.
I calculated somewhere between 3' and 4' of friction loss's for the intake. Add the 15.5' for vertical lift and you end up with about 19' required on the intake side. When I first saw the design I was worried about the pumps being able to pull a prime. I am still a little worried about that.
So my questions is what do I design to? NPSHa (33-19=14 which is greater than 10') looks OK. NSPHr (14 >> 4), or static suction lift? I am guessing that static suction lift has nothing to do with the friction loss's but I would like a clarification on that!
Any help/advise is greatly appreciated!
The intake in the hudson river is a screened inlet (with about 1 ft of loss at the system design point of 150gpm) attached to long radius elbow and then ~1800' of 8" DR-11 HDPE pipe to the pump station on the banks of the river.
Mean low tide is about 15.5' below the centerline of the pump.
Where the line enters the pump house there is 2 8" x 4" Wye's (one feeds each redundant pump). a 4" gate valve, a 4" basket strainer, another 4" gate valve, then a 4"x3" concentric reducer on the inlet of the pumps.
The pumps are Goulds 3796 3x3-13 MTi's with a cut down impeller of 12.875". The pumps are in parallel and one will be in standby while the other is active. Design flow rate is 150gpm at a TDH of 140' The pump spec sheet lists and NPSHa of 10ft, a NPSHr or 4ft (at 150gpm, but the curve does not go below 150gpm). I found that on the goulds website they listed "static suction lift" at 20ft.
I calculated somewhere between 3' and 4' of friction loss's for the intake. Add the 15.5' for vertical lift and you end up with about 19' required on the intake side. When I first saw the design I was worried about the pumps being able to pull a prime. I am still a little worried about that.
So my questions is what do I design to? NPSHa (33-19=14 which is greater than 10') looks OK. NSPHr (14 >> 4), or static suction lift? I am guessing that static suction lift has nothing to do with the friction loss's but I would like a clarification on that!
Any help/advise is greatly appreciated!