First, I would like to say thank you for taking the time to read my post. Second, this is my first post so I hope it is in the right area.

Anyway, I am in the process of designing an accumulator for my companies steam system. We have an electric steam generator designed for 600 lb/h @ 135psig. The steam load goes in 30 second cycles where we draw 4 lb/h in 3 seconds @ 70 psig then the accumulator has 27 seconds to regenerate before the next cycle.

Dropping the steam pressure form 135psig to 70psig yields 5.2% flash.

Can anyone help me out here? I spent numerous hours last weekend running in circles trying to comprehend the Spirax Sarco reading.

THANKS AGAIN!!!
 
Replies continue below

Recommended for you

your ussage is too small for spirax calculator.
calculating acc's is time consuming and sometimes uncertain.
you are shrt injust 1 lb. and need just a small reservoir/accumulator,
you probably need expert advise,
genblr p.s. shodn't be 3lb and not 3lbs/h?
 
Gen8, yes sir it should be 3 lbs and would a dry accumulator work in this application?
 
it would work but it may become larger pv,
wet would be better
gen blr
 