My current project has two buildings that are apparently required to be 'non-combustible' and as such have CMU walls, l.g. steel roof trusses and metal roof deck. The architect wants asphalt shingles which require 3/4" sheathing for a nailing surface.
I'm comfortable designing for lateral forces assuming the wood sheathing is my diaphragm. However, I am not sure how to fasten the sheathing through the decking to ensure diaphragm action, let alone what to use for the decking as its only purpose here is to shield the sheathing from fire.
This, in my opinion, could be easily accomplished by 2 layers of sheetrock on the roof truss bottom chords or cement board, but the architect says it is required.
The questions are:
1. How should the sheathing be fastened? (I'd like to emulate typical 6"oc/12"oc with self tapping screws, but that would seem quite a bit more labor intensive than using 16d nails driven pneumatically).
2. Can the steel deck serve as the diaphragm? I assume it can, but where can shear values be obtained for this? Obviously they are not in the NDS.
3. If it is easier to use the sheathing as the diaphragm as it is required anyway, what should be required for the deck if it is simply serving a purpose of non-combustibility?
I'm comfortable designing for lateral forces assuming the wood sheathing is my diaphragm. However, I am not sure how to fasten the sheathing through the decking to ensure diaphragm action, let alone what to use for the decking as its only purpose here is to shield the sheathing from fire.
This, in my opinion, could be easily accomplished by 2 layers of sheetrock on the roof truss bottom chords or cement board, but the architect says it is required.
The questions are:
1. How should the sheathing be fastened? (I'd like to emulate typical 6"oc/12"oc with self tapping screws, but that would seem quite a bit more labor intensive than using 16d nails driven pneumatically).
2. Can the steel deck serve as the diaphragm? I assume it can, but where can shear values be obtained for this? Obviously they are not in the NDS.
3. If it is easier to use the sheathing as the diaphragm as it is required anyway, what should be required for the deck if it is simply serving a purpose of non-combustibility?