Hello. I am looking at a set of draft residential plans with an engineer friend just to grow my knowledge.
He's handling everything professionally - I'm just trying to expose myself to a different field since I work on bridges mostly.
The plans show a new floor being constructed over existing construction. Typically, wood framing would be used but due to the rising lumber prices they're using steel framing.
I'm a little concerned of the steel members being used.
The HSS 6x6x3/8 seems underdesigned.
Roughly speaking for a 40 psf residential LL and assuming ~15 psf DL, we get a 55 psf total load.
For ASD and a trib width of 23' for the highlighted 21.5' beam in the attachment, we get a uniform load of 1.27 KLF.
Moment Demand ~ 75 kip-ft
Zx ~ 16 in3
Design Moment Capacity with the 1.67 reduction factor and Fy of 46 ksi ~ 37 kip-ft
Am I missing something?