Steel Joist 20 H7 1
Vfigueroa
6
We are evaluating a series of cracks that has been developing during the last month on a lightweigth mezzanine structure. The structure was built on 1985 and five years ago a series of cracks developed on the 2.5 thin concrete slab. The construction drawings describes the joist elements as 20 H7 supporting a 2.5 inches concrete slab and a wire mesh reinforcemnt. The mezzanine slab was rated at that time capable to resit live loads up to 125 psf.
Where can I find the mechanical properties, load tables or any information on that specific type of steel joist.
SJI has the 75 year manual available which has all the info you need for a 20H joist. This is a very good, valuable document you should have.
SJI Publications
I bet we hit the SUBMIT button within a second of each other.
Values from SJI - 1978
20H7: Nominal Depth = 20 in
Resist Moment = 499,000 in-lbs
Max End Reaction = 5400 lbs
Approx WT = 10.7 lbs
Maxmum Tensile Stress= 30,000 psi
If you have the span, I can give you the allowable loads.
I went to SJI seminar and got education credits and free 41st Edition manual for free. It was a great seminar and the breakfast and lunch wasn't bad either. I went to one in Long Beach, California although I live and practice in NY. They have it all throughout the country at various time. Check them out. It was definitely worth the money for me.