When y'all design roof framing (commercial project specifically), do you put an absolute limit on the LL/SL deflection of the roof framing due to anticipated/potential interior partition walls going up to deck with a slip track head condition? My understanding is that typical slip tracks only allow 3/4" or 1" of deflection (one way).
If you have, for example, interior girders spanning 40' and joists spanning 50', to limit the absolute deflection of these members to 1" total (at mid span of both the joist and girder), you would have to design them for a deflection ratio of L/1080.
40'/1080 + 50'/1080 = 1"
I think this is going to result in some rather large roof framing members. Larger than typical I would assume, but I haven't actually run through examples.
Do you design for an absolute total deflection in most cases? Or do you only check it when you know you'll have a full height interior partition wall at a certain location and hope future remodels or tenant buildouts don't create full height partitions in larger deflection areas?
Lastly, if you are designing for a total absolute deflection, how do you typically specify or control what deflection the deferred submittal items should be designed to? I.E. if you have a WF girder beam, do you limit it's deflection to 1/2" and then tell the steel joist or truss supplier to also limit their deflection to 1/2" (ending up with worst case 1" total deflection)?
If you have, for example, interior girders spanning 40' and joists spanning 50', to limit the absolute deflection of these members to 1" total (at mid span of both the joist and girder), you would have to design them for a deflection ratio of L/1080.
40'/1080 + 50'/1080 = 1"
I think this is going to result in some rather large roof framing members. Larger than typical I would assume, but I haven't actually run through examples.
Do you design for an absolute total deflection in most cases? Or do you only check it when you know you'll have a full height interior partition wall at a certain location and hope future remodels or tenant buildouts don't create full height partitions in larger deflection areas?
Lastly, if you are designing for a total absolute deflection, how do you typically specify or control what deflection the deferred submittal items should be designed to? I.E. if you have a WF girder beam, do you limit it's deflection to 1/2" and then tell the steel joist or truss supplier to also limit their deflection to 1/2" (ending up with worst case 1" total deflection)?