I have been reading AISC's design guide 11 on floor vibrations. I need to stiffen an existing bar joist floor for a future loading with vibration. (The existing floor is okay for stress and deflection under the new load.)
From my reading, it seems as if a 'queen post' configuration on the bottom of the existing steel joists is the most effective means. For those of you without this design guide, it states:
"A technique which has been shown to be effective if there is enough ceiling space is to weld or clamp a queen post hanger to the bottom flange of a beam or joist as shown in Figure 7.1c. This arrangement substantially increases the member stiffness. The hanger can be placed around existing ducts and pipes in the ceiling space. Repairs can be carried out at nights or on week-ends by temporarily removing ceiling tiles below each member to be stiffened. The hanger should be prestressed by jacking up the floor before welding or clamping) the last connection."
The figure they reference is a small diagram of a bar joist. The 'queen post' configuration essentially adds a new bottom chord below the existing bottom chord (and any ducts or piping).
My questions are: Has anyone implemented this method? Was it successful? Or, do you have more of a cautionary tale to tell? If a series of joists are stiffened... shouldn't there be some nominal lateral bracing between the queen post bracing system of each joist?
From my reading, it seems as if a 'queen post' configuration on the bottom of the existing steel joists is the most effective means. For those of you without this design guide, it states:
"A technique which has been shown to be effective if there is enough ceiling space is to weld or clamp a queen post hanger to the bottom flange of a beam or joist as shown in Figure 7.1c. This arrangement substantially increases the member stiffness. The hanger can be placed around existing ducts and pipes in the ceiling space. Repairs can be carried out at nights or on week-ends by temporarily removing ceiling tiles below each member to be stiffened. The hanger should be prestressed by jacking up the floor before welding or clamping) the last connection."
The figure they reference is a small diagram of a bar joist. The 'queen post' configuration essentially adds a new bottom chord below the existing bottom chord (and any ducts or piping).
My questions are: Has anyone implemented this method? Was it successful? Or, do you have more of a cautionary tale to tell? If a series of joists are stiffened... shouldn't there be some nominal lateral bracing between the queen post bracing system of each joist?