Inrushman
- Sep 24, 2009
- 12
Hi all,
It has been reported to our department that a new substation has supply by in-out arrangement from an existing double circuit 380kV OHTL, experiences frequent FLASHOVER on the two suspension towers adjacent to the tapping point, the flashovers occured almost at same time daily it is around 6 a.m., where the weather is very humid, i have investigated various causes assuming that the suspension insulators ( Vee Type ) on the existing towers had been slightly tilted during stringing of the cut conductors to the new terminal tower, field investigation by binoculars proofs perfect alignment...the Trip log showed both differential and distance relay trip on all phases on one side, and on center phase - (Blue) on the other phase, one two different days.
I think that some trapped charge is accumulating between the two lines ( continuous and cut one ), and unbalance due to the diffraction angle of the exiting towers ( about 3 degrees ), caused this (potential) over-voltage on certain adjacent towers,...
Any ideas?
Any ideas?