faromic
- Aug 28, 2007
- 52
I have a situation where exterior columns of a 7 story building are flush with the property line at one side of the building. Because of this I have eccentric footings at these locations. I want to design a strap beam at these locations, but am unsure about how to go about this. The footing at the edge of the building is 9'x9' and the other footing at the interior is 13'x13'. They are spaced at 27' on center. This leaves the strap beam length as 12.5'. THe size of the strap beam 24" deep x 36" wide. At first I modelled it as one span with a cantilever but am getting a moment of 900 k*ft. THe loads are pretty high, 500 kips on the edge footing and 1000 k on the interior footing, but the moment just seems high to me. Then I tried to model the beam as a simply supported from edge of footing to edge of footing with a length of 12.5', assuming the footing to beam connections are pin connections. I get approximately the same thing because of the conservativeness of the calculation of the moment.
I have another edge ftg. that connects to an interior ftg which is part of a mat supporting the shear wall core. The strap beam will connect the edge ftg to the mat. From RISA, the output of the moment at the area where I'm going to introduce the strap beam is 44.1 kips. This seems odd since when I compute the moment on a 13'x13 ftg (this ftg is part of the mat) I get a much larger moment. What I did was apply the 44.1 k*ft moment at the edge of the strap beam and add the moment from the analysis of the load from the edge footing.