medeek

Structural
Mar 16, 2013
1,104
Up until now I have checked stud walls for axial and out of plane wind loading using MWFRS wind loads because I was of the understanding that when there is combined loading of a member (ie. axial and bending for a stud wall) one should use MWFRS instead of C&C wind loads.

Typical calcs for a stud wall look like the following link:

http://design.medeek.com/resources/framing/2014-2x6_STUDWALL.pdf

However, after reading through my recently purchased copy of "Guide to the Wind Load Provisions of ASCE 7-10" by Mehta and Coulbourne I've noticed that they are most often calculating wind loads for wall stud loads using C&C and not MWFRS.

Any enlightenment in this matter would be greatly appreciated.


Another related question that has been bugging me for a few days is why is there no C&C wind load diagram for hip roofs with θ > 27 degrees. I've seen many 12/12 pitch hip roofs so this omission seems very glaring to me.
 
Replies continue below

Recommended for you

Based on the paper provided by Rlewistx the correct way to analyze the stud wall would be to:

1) check gravity axial loads. D + L or D + (Lr or S) or D + .75L + .75(Lr or S)
2) Then check bending loads from wind only using C&C at the worst case scenario (zone 5), no axial loads.
3) Then a combined check of axial and wind loads using (MWFRS) wind loads.

What I am missing in my spreadsheet is the C&C bending only load case check (2), which as stated in the whitepaper, is often the controlling load case.
 
Here is an updated stud wall calculation with the missing C&C (bending only) wind load, specified as load case 2.

Updated Stud Wall Calculation

After giving it some thought about Load Case 3, I realized there is actually one more combined load case (D + W). Note that there is no 75% reduction in loads in this case. So to encompass this load case without having to insert yet another load case into the spreadsheet I decided to run the combined gravity and lateral load case all at 100%. This may be a bit conservative but it then ensures that I have covered myself for the D + W load case.

I also decided to use Zone 5 C&C so that I'm also conservative there as well. Note that in this particular case the C&C (bending only) load case governs as expected for a high wind location (155 mph ultimate wind speed).
 