I have a cooling tower with a 2' water level sitting 20' above 3 pumps that routinely swing from 190' to 130' about every 30 seconds. There are suction screens with a bunch of junk on them right in the pan. The suction screens sit on top of 3 respective 48" pipes and below that are vortex breakers for each suction. These 3 pipes feed the suction header to the pumps. The question I have is a loss issue. The difference in water height is about 6" across the screens. So that means a 1/2'(.22 psi) loss in the suction piping is causing the cavitation? It surprises me that the pumps are so close to the NPSHr. Unfortunately, I don't have NPSHr curves for these pumps because they were built before NPSHr curves were imposed on pump curves. I have a hard time believing there is another pluggage downstream of the vortex breaker causing an additional pressure drop, but maybe that is the case.
Thoughts?
-Mike
Thoughts?
-Mike