I apologise in advance for not spotting earlier posts on superheater safety valve (PSV) capacity.
If a SHO PSV had a capacity of 100% MCR, then the steam temperature through the PSV and SH tube temperatures would be the same as for design.
PG-68.2 is interpreted in some places as meaning that the SHO PSV capacity can be typically 15%-25%. Reducing the steam flow to 15% during pressure relief will increase the steam temperature and SH tube temperature. I cannot find any mention of this.
The simple option would seen to go back to first principles and size the capacity of the SHO PSV on either 100% MCR (simple) or determine the actual steam flow rate necessary to keep the tubes and header within their design pressure corresponding to actual temperature experienced at the lower relieving flow. A SH correction for the higher temperature would then be applied to the SHO PSV. I would welcome any comments?
Thanks
If a SHO PSV had a capacity of 100% MCR, then the steam temperature through the PSV and SH tube temperatures would be the same as for design.
PG-68.2 is interpreted in some places as meaning that the SHO PSV capacity can be typically 15%-25%. Reducing the steam flow to 15% during pressure relief will increase the steam temperature and SH tube temperature. I cannot find any mention of this.
The simple option would seen to go back to first principles and size the capacity of the SHO PSV on either 100% MCR (simple) or determine the actual steam flow rate necessary to keep the tubes and header within their design pressure corresponding to actual temperature experienced at the lower relieving flow. A SH correction for the higher temperature would then be applied to the SHO PSV. I would welcome any comments?