@ Marmite, I disagree. In my area when ever a line relies entirely on the earth for fault clearing/detection insulation values increase on everything regardless of source substation grounding. The reasoning behind it is, for example, if a pole with a very high soil resistance has a single phase come in contact with the cross arm the voltage may rise up to full phase potential on the 2 remaining insulators and suppressors given ground resistance is high enough. The impedance is to high to cause a voltage sag equal to or less than the phase neutral voltage.
On a line with all loads being Delta connected there is a good chance line devices would trip, since ground pickup can be set at a very low value. (few amps) However,In a system where the the equipment grounding conductor is also used as a load neutral (multi-grounded neutral system) (which may be the case with the OP), the breaker/reclosers are set often with a very high ground pick up value. In the USA usually 1/3 to 2/3 of the phase pickup value. That combined with high soil resistance may result in over voltage values for an extended period of time without load showing it (ie, voltage drop, flickering)or line equipment clearing.