A few days ago while carrying out some basic maintenance work in a 20kV ring main unit fitted with bushing mounted current transformers the following sequence of events happened:
-While the circuit breaker was in the "open" position and the earth switch was in the "on" position. When we opened the earth switch,at the moment of doing this the bushings became momentarily live with the subsequent risk for the operator, etc.
The three cable bushings had been shorted prior to the opening of the earth switch as a further precaution.
This resulted in the operation of the protection relay which picked up a fault without reaching the trip state thus indicating to us that the bushings only became live for a very short period of time. Approximately 25ms.
Has anybody encountered this kind of problem with ring main units?
I can not name the manufacturer of the switchgear for obvious reasons.
Any information of similar type of occurrences would be of interest.
Thank you all
-While the circuit breaker was in the "open" position and the earth switch was in the "on" position. When we opened the earth switch,at the moment of doing this the bushings became momentarily live with the subsequent risk for the operator, etc.
The three cable bushings had been shorted prior to the opening of the earth switch as a further precaution.
This resulted in the operation of the protection relay which picked up a fault without reaching the trip state thus indicating to us that the bushings only became live for a very short period of time. Approximately 25ms.
Has anybody encountered this kind of problem with ring main units?
I can not name the manufacturer of the switchgear for obvious reasons.
Any information of similar type of occurrences would be of interest.
Thank you all