Hi
I am new to this field, so my explanation may not sound right, so here it goes.
Once I put one generator online (Gen 1) and try to sync the other one (Gen 2) with the help of a synchroscope, it stays on for 8 secs and then trips. No other fault indications. There is a synchronizing relay if that might be a cause.
Things to note:
Before CTs directions change
1. If I sync Gen 1 to Gen 3 or vice versa, Gen 3 KVAR and Ampere meters go really high.
After CTs directions reversal
2. Reversed all 3 CTs on both Gen, now the breaker trips as mentioned earlier. The KVAR meter don't show any reading now and the ampere meter shows around 150 amps on no load.
Also, How do I identify if the CTs are in the right direction with the arrow mark on it?
I am new to this field, so my explanation may not sound right, so here it goes.
Once I put one generator online (Gen 1) and try to sync the other one (Gen 2) with the help of a synchroscope, it stays on for 8 secs and then trips. No other fault indications. There is a synchronizing relay if that might be a cause.
Things to note:
Before CTs directions change
1. If I sync Gen 1 to Gen 3 or vice versa, Gen 3 KVAR and Ampere meters go really high.
After CTs directions reversal
2. Reversed all 3 CTs on both Gen, now the breaker trips as mentioned earlier. The KVAR meter don't show any reading now and the ampere meter shows around 150 amps on no load.
Also, How do I identify if the CTs are in the right direction with the arrow mark on it?