T23 Reheater Tube Fracture in Weld -- Anyone seen this fracture morphology before?
Several T23 reheater tubes failed in a similar manner after less than 6 months and ~250 cycles from commissioning of the HRSG. The circ. fracture originates in the weld, at the front (where you would expect bending force to be greater) then moves into the base metal as it propagates around to the back side. Meanwhile, a ~4" long tear happened on the front side. It seems like there is more than one thing wrong here.
Unfortunately I did not see the header side of the story (another case of repair first, ask questions later), so it is hard to confirm the lack of penetration that me and the repair contractor suspected.
Particulars: 2" T23, welded to P22 header with manual TIG, ER9018-B3, PWHT. Unknown tube origin, but they are significantly older than the plant. All zones appear to have normal microstructure (no ferrite at least). The correct filler was used. Weld hardness is 285HV1, HAZ up to 335HV1, base ~192HV1. I have found both tube surfaces decarburized. Scattered corrosion pits up to 3 mils deep on outer surface. A few very short secondary cracks and sometimes oxide along prior austenite GBs.
Any thoughts or suggestions? The hardness seems on the high side for a PWHT joint. I thought about reheat cracking, but did not think that can affect the weld also(?)
I am a newbie here so I hope this gets posted correctly ...
Several T23 reheater tubes failed in a similar manner after less than 6 months and ~250 cycles from commissioning of the HRSG. The circ. fracture originates in the weld, at the front (where you would expect bending force to be greater) then moves into the base metal as it propagates around to the back side. Meanwhile, a ~4" long tear happened on the front side. It seems like there is more than one thing wrong here.
Unfortunately I did not see the header side of the story (another case of repair first, ask questions later), so it is hard to confirm the lack of penetration that me and the repair contractor suspected.
Particulars: 2" T23, welded to P22 header with manual TIG, ER9018-B3, PWHT. Unknown tube origin, but they are significantly older than the plant. All zones appear to have normal microstructure (no ferrite at least). The correct filler was used. Weld hardness is 285HV1, HAZ up to 335HV1, base ~192HV1. I have found both tube surfaces decarburized. Scattered corrosion pits up to 3 mils deep on outer surface. A few very short secondary cracks and sometimes oxide along prior austenite GBs.
Any thoughts or suggestions? The hardness seems on the high side for a PWHT joint. I thought about reheat cracking, but did not think that can affect the weld also(?)