I am trying to figure out the temperature of the air that I am ventilating from a pump room to decide whether it needs to be exhausted to the outdoors. I have (2)20hp pumps, I have done a rule of thumb to figure out the Btuh that these will be giving off and came up with 15026 Btuh. (110 Watts per hp> (110*40=4400 Watts > converted to Btuh = 15026). I am moving 1000 cfm out of the room and intaking the same. The room is approximately 100 sq. ft.
 
Replies continue below

Recommended for you

Thanks for the reply. I am sorry, I really should have clarified that I don't have a good concept of what the intake air temperature is going to be. This room is in a ventilated garage that is partially buried underground. I am obviously trying to figure out worst case scenario. This building is in South Florida.
 
First, I think your heat gain from the motors is low. ASHRAE has a guideline for this, and a 20hp pump with both motor and pump in the same space releases 58,500 btu/hr. If both pumps are running, that's 117,000 btu/hr.

The air temperature rise = btu/hr divided by 1.08 x cfm.

If both pumps run continuously, this will be an extremely hot room.

 
Thanks for the post. I agree that the 13 degree dT seems very low for (2) 20hp pumps. Can you tell me where ASHRAE states the guideline for the pump heat gain?
 