Hi Community
I read part of ACI Commentary 2243r_95.And I was looking for the length of the building that don't require temperature study(I already know that is almost less than 45-50 m),but I need the reference for this data, so any suggestion?
Also AS per my reading in ACI 2243r_95 I found that expansion joint (Or as refer by the manual is isolation joint ,since expansion joint allow movement in one direction and prevent shear)should extend in the whole building up to the foundation, Actually this logically acceptable since the volumetric change that may occur to the isolated footings is negligible, but I have the following questions?
1)If I have raft foundation, is it right to separate the foundation as well, since the raft is huge and temperature changes will have huge stresses or should I reinforced it to theses stresses and never separate the raft?(Manual Saying only up to the foundation level)
2. If the raft or isolated footings is not part of expansion joints (isolation is up to the foundation ), hence I have to take mass of both adjacent building in the calculations(but designers don’t do that??)
The reason of taking both buildings mass .is they are still connected at the foundation level!!!!
Thanks
I read part of ACI Commentary 2243r_95.And I was looking for the length of the building that don't require temperature study(I already know that is almost less than 45-50 m),but I need the reference for this data, so any suggestion?
Also AS per my reading in ACI 2243r_95 I found that expansion joint (Or as refer by the manual is isolation joint ,since expansion joint allow movement in one direction and prevent shear)should extend in the whole building up to the foundation, Actually this logically acceptable since the volumetric change that may occur to the isolated footings is negligible, but I have the following questions?
1)If I have raft foundation, is it right to separate the foundation as well, since the raft is huge and temperature changes will have huge stresses or should I reinforced it to theses stresses and never separate the raft?(Manual Saying only up to the foundation level)
2. If the raft or isolated footings is not part of expansion joints (isolation is up to the foundation ), hence I have to take mass of both adjacent building in the calculations(but designers don’t do that??)
The reason of taking both buildings mass .is they are still connected at the foundation level!!!!
Thanks