What is the purpose of a tertiary winding on a transformer?
 
Replies continue below

Recommended for you

Sometimes to have another voltage available, sometimes to provide a path for third harmonic currents in a core form three phase transformer.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Also the presence of the teriary winding redistributes inbalanced currents which minimises the effect upstream.

Regards
Marmite
 
robertplant

In Germany a tertiary winding is called "Ausgleichswickung". This can be translated to "compensation winding" or "equalizer winding", which very well explains the purpose of such a winding. A tertiary winding is a winding which usually is an internal winding, not transmitting power to the outside. Tertiary windings are always of the delta type, in most cases designed for only 6 kV. The purpose of a tertiary winding is to maintain a perfect Ampere-turn balance on all three core legs of a wye/wye transformer, regardless of the star point load. The majority of the HV grid coupling transformers are of the wye/wye type as a HV delta winding is very expensive because of the extra insulation required (a delta winding has 73% more turns than a wye winding, the copper weight is about the same). Wye/wye transformers with a tertiary winding are permitted to carry a full load star point current. Without a tertiary winding some standards are limiting the star point load current to 10%, or less, in order to avoid excessive voltage unsymmetry.

You may also look into threads 242-114285 and 238-125717 for additional information.

Regards

Wolf
 
wolf39 said:
in most cases designed for only 6 kV
Not even close to being true; I've never seen one less than about twice that voltage. They can probably be anything the transformer purchaser wants to specify. Tertiary winding are also often used for station services.
 
Also, three winding transformers are fairly popular in large industrial facilities for serving two medium voltage buses from a single primary. I have also seen 4160 V secondary and 480 V tertiary.
 
David:

Thanks for your comment.

If the transformer purchaser wants a third (active) winding for station services, he gets it, of course. In such case he can specify any voltage. A third winding used for station services, for instance, has its specific purpose. This is obvious and I believe that Roberts question didn't go this direction. I assumed that he wanted to know what a "hidden", i.e. not power transmitting third (tertiary) winding, is for. This I tried to explain.

The transformer designer tries to keep the voltage of a compensation (tertiary) winding low for economical reasons. Still, you are right by questioning my 6 kV figure, which I herewith withdraw. The design voltage of a compensation (tertiary) winding can be as high as 30 kV, and even higher, depending on the transformer output and voltage. A 6 kV figure may be reasonable for, lets say, a 20 MVA/110 kV transformer.

Regards

Wolf
 
We have several 10MVA,33KV/4KV oil filled grounded wye grounded wye formerally used on utility applications now feeding 4 KV motors. They have a delta tertiary winding which is not brough out of the transformer used for stabilization since I expect the core is of three leg design.
JIM
 