Testing of 433V main power panels

Status
Not open for further replies.

myna68

Electrical
Sep 12, 2003
1
Hello all,
Could any tell me what are all the tests to be conducted for accepting the main power panel . I would also like to know both type and routine tests to be conducted on any main power panel.

Thankyou
chandrashekhar
 
Replies continue below

Recommended for you

Suggestion: Specifications for the project or installed hardware should not be ruled out. It may contain special tests that are not listed in 2003 NETA Acceptance Testing Specs. These NETA specs are for architects and architectural engineering firms. They are usually used very carefully since they refer to various industry standards.
 
There may also be specific requirements laid down by the regulators in your country. I guess from the voltage you could be either Australian based or perhaps somewhere in South Africa?


Bung
Life is non-linear...
 
433 volt is the old UK standard for the secondary of a distribution transformer. Therefore I assume the panels has been supplied to IEC 60439 and this can used as a bsis for your type tests.
 