Greetings every senior engineers!
I have a basic question on how to exactly calculate the pressure on the pump suction side, and then matches the practical pressure gauge reading on pump suction side?
First I am using the NPSHa equation.
1atm+H(static)-H(vapor)-H(suction pipe loss)=NPSHa <absolute value>
1atm: I convert it to approximately 10m
H(static): the water source surface level is above the pump centerline for 1.5m
H(vapor): the water is 80 Celsius, so the vapor pressure is 4.83m
H(suction pipe loss): the length is about 2m, carbon steel pipe, and the inner diameter is 36mm, in this part I would like to assume the pipe loss is 2m.
So sum up the above values, 10m+1.5m-4.83m-2m=4.67m < absolute value>
Then 4.67m-10m=-5.33m=-0.533kg/cm^2 <gauge value>
But in the practical gauge reading on the pump suction side is +0.2kg/cm^2.
Thus I don't know why my theoretical value does not matches the practical gauge reading? and what makes the difference between it?
Later I found another question, I found that there is no any contribution by the pump itself, in my assumption there ought to be a force created by the pump which helps the pump to suck in the water.
Thus I would like to ask is it the factor I missed which cause my theoretical calculation can't matches the practical gauge reading on the pump suction side?
And if it does, how could I calculate the sucking in pressure generated by pump?
My centrifugal pump's rated Q is 4.8kg/hr, rated H is 120, 3600 rpm.
Thank you for reading my lengthy description of my question, truly thank you!
I have a basic question on how to exactly calculate the pressure on the pump suction side, and then matches the practical pressure gauge reading on pump suction side?
First I am using the NPSHa equation.
1atm+H(static)-H(vapor)-H(suction pipe loss)=NPSHa <absolute value>
1atm: I convert it to approximately 10m
H(static): the water source surface level is above the pump centerline for 1.5m
H(vapor): the water is 80 Celsius, so the vapor pressure is 4.83m
H(suction pipe loss): the length is about 2m, carbon steel pipe, and the inner diameter is 36mm, in this part I would like to assume the pipe loss is 2m.
So sum up the above values, 10m+1.5m-4.83m-2m=4.67m < absolute value>
Then 4.67m-10m=-5.33m=-0.533kg/cm^2 <gauge value>
But in the practical gauge reading on the pump suction side is +0.2kg/cm^2.
Thus I don't know why my theoretical value does not matches the practical gauge reading? and what makes the difference between it?
Later I found another question, I found that there is no any contribution by the pump itself, in my assumption there ought to be a force created by the pump which helps the pump to suck in the water.
Thus I would like to ask is it the factor I missed which cause my theoretical calculation can't matches the practical gauge reading on the pump suction side?
And if it does, how could I calculate the sucking in pressure generated by pump?
My centrifugal pump's rated Q is 4.8kg/hr, rated H is 120, 3600 rpm.
Thank you for reading my lengthy description of my question, truly thank you!