GalileoG
Structural
- Feb 17, 2007
- 467
All,
I am currently evaluating a buried concrete box structure where the roof slab is at grade level. There is concrete deterioration on the roof slab (delaminated concrete, corroded rebar) that will be rehabilitated. This deterioration was caused by water infiltration as the roof slab is exposed to the elements. I want to extend the service life of this structure by adding a thin concrete overlay no more than 3” thick - as I will have issues with grading if I go thicker than that. The structure has the reserve capacity to take the extra weight, so that is not a problem.
I am looking for tips to properly detail this thin concrete overlay so that cracking will be mitigated. I am thinking about reinforcing it with stainless steel welded wire mesh at mid-depth of concrete overlay, and doweling the overlay to the parent concrete at 5’ intervals in both orthogonal directions. The dowels would help prevent debonding between the overlay and the parent concrete.
Now about the joints…
The overlay will have expansion joints (polyurethane caulking) to match location of roof slab expansion joints, which are 80’ apart along the length of the slab. The slab is 20’ wide.
What are the requirements for contraction joints? Do I need them for a thin concrete overlay? How far apart should these joints be? Do I need to terminate the wire mesh at contraction joints (this would be complicated)? How should the joint be detailed? I am familiar with contraction joints for regular slabs, but I have never dealt with a thin concrete overlay before - any help here would be very much appreciated!
I am currently evaluating a buried concrete box structure where the roof slab is at grade level. There is concrete deterioration on the roof slab (delaminated concrete, corroded rebar) that will be rehabilitated. This deterioration was caused by water infiltration as the roof slab is exposed to the elements. I want to extend the service life of this structure by adding a thin concrete overlay no more than 3” thick - as I will have issues with grading if I go thicker than that. The structure has the reserve capacity to take the extra weight, so that is not a problem.
I am looking for tips to properly detail this thin concrete overlay so that cracking will be mitigated. I am thinking about reinforcing it with stainless steel welded wire mesh at mid-depth of concrete overlay, and doweling the overlay to the parent concrete at 5’ intervals in both orthogonal directions. The dowels would help prevent debonding between the overlay and the parent concrete.
Now about the joints…
The overlay will have expansion joints (polyurethane caulking) to match location of roof slab expansion joints, which are 80’ apart along the length of the slab. The slab is 20’ wide.
What are the requirements for contraction joints? Do I need them for a thin concrete overlay? How far apart should these joints be? Do I need to terminate the wire mesh at contraction joints (this would be complicated)? How should the joint be detailed? I am familiar with contraction joints for regular slabs, but I have never dealt with a thin concrete overlay before - any help here would be very much appreciated!