JSA
Structural
- May 28, 2001
- 24
We're looking to approve a thin, bonded topping slab. The substrate is a cast-in-place, structural concrete slab 8" to 9 1/4" thick spanning 28-feet, built in 1950 and designed for 125psf. The structural floor system is a two-way slab.
For a renovation project, the architect has specified "floor leveling underlayment" for all floors.
As an alternate, the contractor proposes a hard rock concrete topping, 1.25" minimimum to 2.5" maximum +/- thickness, 3/8" rock. The proposal anticipates significant construction cost savings, but obviously, if unsuccessful (extensive cracking, etc.) mitigation costs could be enormous. Fork-trucks are planned in some areas.
Technical concerns seem to be limited to curling. Shotblasting, followed by watering the surface is planned. Proposed is a 3-day water cure, after which we're considering a curing compound. Also, it seems to be that bond testing at the edges (potential curling area) would be appropriate.
Any opinions or thoughts that would helpful at assuring a successful application?
For a renovation project, the architect has specified "floor leveling underlayment" for all floors.
As an alternate, the contractor proposes a hard rock concrete topping, 1.25" minimimum to 2.5" maximum +/- thickness, 3/8" rock. The proposal anticipates significant construction cost savings, but obviously, if unsuccessful (extensive cracking, etc.) mitigation costs could be enormous. Fork-trucks are planned in some areas.
Technical concerns seem to be limited to curling. Shotblasting, followed by watering the surface is planned. Proposed is a 3-day water cure, after which we're considering a curing compound. Also, it seems to be that bond testing at the edges (potential curling area) would be appropriate.
Any opinions or thoughts that would helpful at assuring a successful application?