volkanksr
Electrical
- Aug 22, 2006
- 9
Hello everybody,
I need to calculate %R+ resistance and %X+ reactance values of primary-secondary, primary-tertiary and secondary-tertiary windings. Transformer information :
120/60/60 MVA
154/11/11 kV
Uk: 16%/16%/16%
Po: 40 kW
Pk: 400 kW
Io: %0.25
Please send your calculation results, formulas or any related document about this topic.
best regards,
vlk
I need to calculate %R+ resistance and %X+ reactance values of primary-secondary, primary-tertiary and secondary-tertiary windings. Transformer information :
120/60/60 MVA
154/11/11 kV
Uk: 16%/16%/16%
Po: 40 kW
Pk: 400 kW
Io: %0.25
Please send your calculation results, formulas or any related document about this topic.
best regards,
vlk