Three Winding Transformer Impedance Calculation

Status
Not open for further replies.

volkanksr

Electrical
Aug 22, 2006
9
Hello everybody,

I need to calculate %R+ resistance and %X+ reactance values of primary-secondary, primary-tertiary and secondary-tertiary windings. Transformer information :

120/60/60 MVA
154/11/11 kV
Uk: 16%/16%/16%
Po: 40 kW
Pk: 400 kW
Io: %0.25

Please send your calculation results, formulas or any related document about this topic.

best regards,

vlk
 
Replies continue below

Recommended for you

Look at either of Blackburn's books, the Relay book or the Symmetrical Components book.
 
I am using these formulas . Is it right to use these ones or do you have other way to calculate these resistance and reactance values?

Zb=(Ub*Ub)/Sb where Ub:154 kV Sb:110 MVA

R1: (Psc*Un*Un)/(2.Sn*Sn) ohms
R2=R3=2R1

R1_2= R1+R2
R1_3= R1+R3
R2_3= R2+R3

R1_2(Per Unit)= R1_2/Zb

Thanks for your help