sneja
Electrical
- Oct 24, 2002
- 7
I need to set an overall differential protection for track transformer which is fed from three phase system with rated voltage of 400kV. There is two secondary winding with rated voltage 25kV. For a single-phase transformer in isolation, there is no zero sequence impedance, as the zero phase sequence component represents the residual voltage or current which is present in a three phase circuit under fault conditions when a fourth wire is present either as a direct metallic connection or as a double earth on the system. For a single phase transformer will depend on the other components in the system. Where zero sequence impedance can not flow in the lines on both sides the zero phase sequence impedance is open circuited and it is thus equal to infinity in the relation to the series network. Since the LV side of the track transformer is single phase there can be no zero sequence current flowing in LV side and the transformer zero phase sequence impedance is infinity. To set the protection I need to calculate the through fault current at fault on the LV side. Which method shall I use to determine single phase fault current at LV side? I know the fault level of the source and the transformer impedance. Is it simply ignoring the zero sequence component and using the known method for unbalance fault calculation? Or there is something else I have to consider or assume when I do the calculations?