Ties for wall vertical reinforcement 9

Status
Not open for further replies.

WARose

Structural
Mar 17, 2011
5,594
I have a feeling what the answer is on this one......but I'll ask anyway ([smile])......Does anyone know of anyway (via a code anywhere) that allows you to consider a single layer/curtain of vertical wall reinforcement as "tied' via the horizontal steel? The way I've always read ACI code.....you need to have 2 layers/curtains of vertical steel, with ties between them in order to call it tied as per code.

Basically what I have is: a wall with a single layer of vertical reinforcement (and a horizontal layer as well). I'd like to use that steel as compression steel (for a vertical load on the wall).....but it's not tied. It's a pretty short wall (4' high, 10" thick).

 
Replies continue below

Recommended for you

Yes - I see it. Seems like that's been now relegated to only columns and pilasters (vs. walls) in later editions while the 05 edition simply refers to compression in masonry.

Check out Eng-Tips Forum's Policies here:
faq731-376
 
Well, sort of. I guess WARose should respond on that, though.



Check out Eng-Tips Forum's Policies here:
faq731-376
 
Koot,

That load reversal style of failure is one of the banes of concrete construction in seismic design. You get load reversal failure, then you cycle a few times and the concrete disintegrates. Then you lose the compression or shear load path because you just have a bunch of bars hanging in the air and bad things happen. This is why tie and stirrup detailing are a big deal in concrete seismic systems.
 
I consider it answered. I actually had forgotten about that section of ACI that the debate broke out about.

That reference i posted above (from the NZ code) appears in other forms in other references I have (in a more usable form).....when I get a chance, I'm going to mess around a bit and see what sort of concrete strains correspond to minimum tie areas (as per ACI 318 vs. NZ code).

EDIT: And by the way, thanks to everyone who participated.

 
@TLHS: agreed. I was pretty careful to exclude seismic in all of my comments. That's actually something that I've come to resent a bit. Nowadays, I feel as though I'm obligated to preface every damn thing that comes of my mouth with "..unless it's seismic..."

 
Koot, wasn't really disagreeing or pointing out a problem. Just expanding on your hinge zone caveat.



 
Resurrecting this thread to close loop on the errata and code updates referenced by JAE above. Looks like things have formally changed here.

Previous language in ACI 318-14:
Capture_nctstc_rvveen.png


Language from ACI 318-14 errata:
Capture_pyt0lw.png


Current language in ACI 318-19:
Capture_son6ba.png
 
whew. All is right with the world. I can calm down now!