SrChemE
Chemical
- May 6, 2016
- 54
Hello,
During cold weather conditions we are experiencing freezing on a system that is injected downstream of a toluene line installation. It has gotten too cold and the incoming line freezes at the injection point even so it is heat traced and insulated. (the toluene line is not heat traced and insulated, just the other line that is injected into a separate nozzle).
Due to this freezing problem, we are considering heat tracing the toluene line with a 5 W/ft BSX self-regulating heat trace, but there is the concern of toluene being highly flammable.
We would like to add a self-regulating heat trace on the toluene line prior to the injection orifice and after a control valve, usse a temperature regulator with two pipe temperature indications one for control and one for high temperature cut off. Control temperature will be set for 50 F. (To ensure the temperature of toluene does not reach an unsafe level, dual temperature indications will be installed. One will be the control to the self-regulating heat trace and the other is a high temperature shut off.)
Due to the flammability of Toluene, the Electrical Classification was reviewed, the non-welded piping connections are listed as Class I Division 2. All heat trace and components to be installed are Class 1 Div 2 rated as well. The selected heat trace and installation will meet or exceeds the Class I, Division 2 Group D rating.
Suggestions on how to design this safely and what to consider will be greatly appreciated.
Thank you,
Sarah
During cold weather conditions we are experiencing freezing on a system that is injected downstream of a toluene line installation. It has gotten too cold and the incoming line freezes at the injection point even so it is heat traced and insulated. (the toluene line is not heat traced and insulated, just the other line that is injected into a separate nozzle).
Due to this freezing problem, we are considering heat tracing the toluene line with a 5 W/ft BSX self-regulating heat trace, but there is the concern of toluene being highly flammable.
We would like to add a self-regulating heat trace on the toluene line prior to the injection orifice and after a control valve, usse a temperature regulator with two pipe temperature indications one for control and one for high temperature cut off. Control temperature will be set for 50 F. (To ensure the temperature of toluene does not reach an unsafe level, dual temperature indications will be installed. One will be the control to the self-regulating heat trace and the other is a high temperature shut off.)
Due to the flammability of Toluene, the Electrical Classification was reviewed, the non-welded piping connections are listed as Class I Division 2. All heat trace and components to be installed are Class 1 Div 2 rated as well. The selected heat trace and installation will meet or exceeds the Class I, Division 2 Group D rating.
Suggestions on how to design this safely and what to consider will be greatly appreciated.
Thank you,
Sarah