Mondy
Electrical
- Jul 4, 2003
- 37
Hi All
Can anyone help me with the calculations involved in a transformer short circuit impedance test. I have the following data:
Transformer rated voltage =230v
Transformer rated power = 960VA
Secondary short circuited during test
ambient temperature during test = 22 deg.C
Measured impedance voltage Ez = 3.55v at 50% of rated current and at the transformers rated frequency (50Hz)
Supplied current = 2.188 average amps
Measured copper loss CuW = 7.51W at 50% of rated current and at the transformers rated frequency (50Hz)
Impedance voltage (Ez) and Load Loss (CuW) corrected to 100% of the rated current and a reference temperature of 80deg.C resulting in:
Short circuit resistance Er = 3.84%
Short circuit impedance Ez = 3.87%
Short circuit reactance Ex = 0.51%
Copper Loss CuW @ 100% load = 36.84W
I assume that the Ez of 3.84% is calculated from the 3.55v @ 50% of rated current (although I cannot get it to add up) and then the reactance Ex = 0.51 derived from
Sqr(Ez 3.87^2 - Er 3.84^2)
and Er = 36.84W * 10 /960VA
as usual, but I cant get it to add up. Or is the Ex = 0.51 calculated and then added in quadrature to come up with the Ez = 3.87%
Can anyone get these figures to make sense as I cannot get them to correlate and I can only assume I am not taking into account something in the correction of the parameters measured at 50% of rated load to 100% rated load and 80 deg.C reference temperature?
Cheers
Ray
Can anyone help me with the calculations involved in a transformer short circuit impedance test. I have the following data:
Transformer rated voltage =230v
Transformer rated power = 960VA
Secondary short circuited during test
ambient temperature during test = 22 deg.C
Measured impedance voltage Ez = 3.55v at 50% of rated current and at the transformers rated frequency (50Hz)
Supplied current = 2.188 average amps
Measured copper loss CuW = 7.51W at 50% of rated current and at the transformers rated frequency (50Hz)
Impedance voltage (Ez) and Load Loss (CuW) corrected to 100% of the rated current and a reference temperature of 80deg.C resulting in:
Short circuit resistance Er = 3.84%
Short circuit impedance Ez = 3.87%
Short circuit reactance Ex = 0.51%
Copper Loss CuW @ 100% load = 36.84W
I assume that the Ez of 3.84% is calculated from the 3.55v @ 50% of rated current (although I cannot get it to add up) and then the reactance Ex = 0.51 derived from
Sqr(Ez 3.87^2 - Er 3.84^2)
and Er = 36.84W * 10 /960VA
as usual, but I cant get it to add up. Or is the Ex = 0.51 calculated and then added in quadrature to come up with the Ez = 3.87%
Can anyone get these figures to make sense as I cannot get them to correlate and I can only assume I am not taking into account something in the correction of the parameters measured at 50% of rated load to 100% rated load and 80 deg.C reference temperature?
Cheers
Ray