Typical X/R ratio 1

Status
Not open for further replies.

lz5pl

Electrical
Feb 6, 2007
313
I try to simulate a small industrial network using ELPEK software. For the source I have value of short circuit current. But for defining a feeder internal R and X are required and I haven't r/x ratio. I am looking for advice regarding typical values. I know they will vary, but I should start from somewhere.
This problem appears every time I have to simulate some network. Usually the only information available from the customer is short circuit power or current.

------------------------
It may be like this in theory and practice, but in real life it is completely different.
The favourite sentence of my army sergeant
 
Replies continue below

Recommended for you

Thank you Slava. I am on 6 kV side, so I will start with x/r=2 , it should be sufficient for the first approximation.
Source is 110/6,3 kV, 125 MVA power transformer, supplied through very short 110 kV line from a big system substation 400/110 kV.

------------------------
It may be like this in theory and practice, but in real life it is completely different.
The favourite sentence of my army sergeant
 
Hi.
For this trafo see following data:
 
Thanks for the tables Slava.
Respectfully
 