Pipis118
Mechanical
- Feb 27, 2023
- 2
Hi All,
I'm interested in parties/ cases of where people have had experience around reporting a case of imminent danger to the HSEx or enforcing authority (UK)and what the outcome was.
Regulation 10 requires that where an inspection under the written scheme of examination (WSE)identifies an instance where the equipment may give rise to imminent danger if returned to service/ continued in service without certain repairs or actions taken to remove that level of risk.
I'm aware that the HSEx must be informed of the issue within 14 days of the finding and the user/ owner must be informed at the earliest opportunity before the inspector/ competent person leaves site.
An example I was given was around a relief device which was returned post overhaul, and the pop test revealed the valve lifted at 110% CDTP. An auditor stated that was a case of imminent danger to the system int eh it could be over pressurised.
My take was that it wasn't that black and white, the system was relatively new, in very good condition (on plant air duty) and had been pressure tested to 1.5 times design pressure.
If the system was 20 years old, falling apart and poorly maintained i would have had a different take.
Wondering what cases people have had in the UK. Insurance company CP's tend to report on cases of reg 10 fairly frequently but other 3rd party CP's tend to be far fewer.
Thanks in advance & hope it makes sense...
I'm interested in parties/ cases of where people have had experience around reporting a case of imminent danger to the HSEx or enforcing authority (UK)and what the outcome was.
Regulation 10 requires that where an inspection under the written scheme of examination (WSE)identifies an instance where the equipment may give rise to imminent danger if returned to service/ continued in service without certain repairs or actions taken to remove that level of risk.
I'm aware that the HSEx must be informed of the issue within 14 days of the finding and the user/ owner must be informed at the earliest opportunity before the inspector/ competent person leaves site.
An example I was given was around a relief device which was returned post overhaul, and the pop test revealed the valve lifted at 110% CDTP. An auditor stated that was a case of imminent danger to the system int eh it could be over pressurised.
My take was that it wasn't that black and white, the system was relatively new, in very good condition (on plant air duty) and had been pressure tested to 1.5 times design pressure.
If the system was 20 years old, falling apart and poorly maintained i would have had a different take.
Wondering what cases people have had in the UK. Insurance company CP's tend to report on cases of reg 10 fairly frequently but other 3rd party CP's tend to be far fewer.
Thanks in advance & hope it makes sense...