I want to know the implications of connecting unbalanced delta load to secondary (Star Winding) of transformer.
Thanks.
An unbalanced delta load. That means no neutral, so there shouldn't be any current in it.
It depends on the primary winding. If it is a delta winding, then your ampere-turns will be OK. If it is a wye winding - the ampere-turns do not agree so well and you get voltage drops.
Is it a Y/Y or a D/Y transformer?
Gunnar Englund
Shouldn't be a problem then.
Gunnar Englund
Dear Skogsgurra
Can you suggest some reading material on this topic ?
Thanks.
You will have unbalanced line currents on the delta side.
Bill
"Why not the best?"
Jimmy Carter
Is the centre of the star point earthed?
Sorry to be a bore. But, if there's a wye secondary, and the load is delta. Where can any neutral current flow?
Gunnar Englund
OK, if it is earthed then there is no big deal. If it was floating, then that's a different kettle of fish.
Egad, belay all that. I've just realised that the load is delta (thanks, Gunnar - and an abashed grin). Doesn't matter if it is earthed or not.
Let me try. There is a neutral point at the transformer wye winding, none at the delta load, and no neutral current involved with this load.
@Skogsgurra "If it is a wye winding - the ampere-turns do not agree so well..."
Why wouldn't the amp-turns match in this case?