Uncoupled Motor Load

Status
Not open for further replies.

BECREZ

Electrical
Jun 14, 2002
17
0
0
US
We are testing out a pulverizer motor (800 HP @4.16kV) and it is running uncoupled. The amperage reading is about 80% of the rated FLA. This seems high to me and was wondering what the rule of thumb (if any) regarding comparing the running current coupled versus uncoupled?

Thanks
 
Replies continue below

Recommended for you

Hello becrez

When you operate a motor uncoupled, you effectively get the magnetising current of the motor.
On very small motors, this can be as high as 60% of the rated current of the motor. On large motors it is typically around 20% of the motor rating. Liquid cooled motors will often have a higher magnetising current due to increased operating flux in the iron.
I would say at 80% of the rated current, you have a problem and I would definitely not operate that motor without confirmation from the manufacturer.

An excessive magnetising current is usually caused by the V/Hz ratio being higher than the design ratio. This increases the iron flux and results in core saturation and great heat loss in the core.
Typically, this is caused by operating a 60Hz motor at it's desing voltage but at 50 Hz, or by operating at the correct frequency and a higher voltage. On low voltage machines, this can be caused by operating a star designed motor in delta on the star designed voltage.

Let us know the outcome,
Best regards,

Mark Empson
 
80% no-load current is high. Was the stator rewound ? If so, the rewinder made mistakes.

If it is new, as Mark says, check whether your supply matches the name-plate values (Voltage, frequency, stator connection etc.)


* Basically, I would like a full-time job on part-time basis *
 
Rule of thumb for large motors such as these
no-load current ~ 20% of FLA for 2-pole
no-load current ~ 50% of FLA for slow speed motor (ex 10-pole)

=====================================
Eng-tips forums: The best place on the web for engineering discussions.
 
Does the motor have a Power Factor rating?
the reactive current as a percentage of the full load current may be calculated from the power factor rating.
(1-(P.F.^2))^.5
For a full load Power Factor of 75%
(1-(.75^2))^.5
(1- .5625)^.5
Reactive current equals 66% of full load current.
If we assume 30% losses at no load we get
(.3^2 + .66^2)^.5 = 72% of full load.
These assumptions are getting unrealistic for normal motors and we are still short of 89% of full load current.
I vote with the others, check the connections. It may be connected delta instead of wye.
respectfully
 
Hello BECREZ.

I think you have a Synchronous Motor. It could be operating without exitation at all or being set to opearte around 80% leading PF at full load. Under both conditions the motor reactive current is very high, taking or returning reactive power to the line. Check the exitation setup while running under no load condition. If you confirm the description above, the motor is OK and the high no load current is normal. As a test change the excitation current up and down, the motor line current must decrease to a minimum and then increase again, that is known as the "V" curve of the motor current.
 
That's a handy relationship.

I guess if you have an efficiency rating on your nameplate, you can use it to calculate the power factor
pf = sqrt(3)*FLA * Vnameplate / (eff * nameplate Horsepower)

with suitable conversion from horsepower to watts to make the units work.

Then plug p.f. into waross' equation to estimate no-load current.

=====================================
Eng-tips forums: The best place on the web for engineering discussions.
 
OK, not quite. But you know what I meant.
pf = nameplate horespower/(eff * sqrt(3)*FLA * Vnameplate)
again with unit conversions needed.

=====================================
Eng-tips forums: The best place on the web for engineering discussions.
 
BECREZ,

You need to confirm motor type and speed. We have a 16 pole, 800HP, 4.16kV induction machine with no load current exactly 61.5% of full load current.
 
becrez,

Could your reading be an instrumentation or measurement error ? (Improper CT ratio or meter multiplication factor ?)

Many questions but no replies !!!


* Basically, I would like a full-time job on part-time basis *
 
We queried the vendor and they responded that this was in the normal range. I had my doubts and therefore my question. The CT's and readings all checked out fine and motor temperature was O.K. also.
 
I feel the same as you, jraef.
I am wondering if this is a "High slip" motor for pulverizer duty.
I would feel comfortable with these readings if the motor is a special motor designed for shock loading and high momentary overloads.
The motor on a "Hammer hog" type pulverizer may need to withstand shock loading and momentary overloads.
respectfully
 
Yes, maybe Design D. Pulverizers often have massive flywheels so they need fast recovery of speed when a big load passes through. I've seen old mill motors with 15 and 25% slip for applications like that, but I never worked with them uncoupled. I didn't know the NLA could be that high, but it makes sense.

Eng-Tips: Help for your job, not for your homework Read faq731-376 [pirate]
 
can someone explain to me why it makes sense that a design D motor would have high magnetizing current?

I'm not disagreeing but I don't see why it follows.

=====================================