Dear members,
for the above mentioned installation conditions for underground cables a thermal calculation is usually recommended. However in case we want to make a rough estimation of the cable amapcity derating what is the recommended factor to be used? According to available references from textbooks and manufacturer catalouge this factor varies between 0,8 and 0,9.
Any recommendations or suggestions based on experience?
Please notice that the subject here is a factor which is additional for the other factors of ground temperature, grouping, soil thermal resistivity.
Thank you.
Adam
for the above mentioned installation conditions for underground cables a thermal calculation is usually recommended. However in case we want to make a rough estimation of the cable amapcity derating what is the recommended factor to be used? According to available references from textbooks and manufacturer catalouge this factor varies between 0,8 and 0,9.