underground tunnels
is there a good book about tunnel engineering for underground power cables ?
thanx
Suggestion: Visit
for: "Keep up with conductors at ICC"
and
Underground Power Cables
by S. Y. King, N. A. Halfter
Underground power cables : some aspects of their thermal environment by S. Y. King
Are you looking for info on the design of the tunnel itself or use of power cables within a tunnel? What size tunnel are you considering?
I'm looking for the information on the tunnel including needed facilities and the techniques for cabling in the tunnel .dimensins are apprximately 2 by 2.5 meter.
Have you considered posting in the civil engineering forum?
I don't know of any book that deal with this specifically. I would think the main concerns would be temperature, possible corrosive or wet environment, type of cable jacket, and means for supporting the cables.
temperature: you need to know what it is. Utility tunnels with steam pipes can be very hot, which may require derating the cable ampacity.
corrosion: personal experience tells me to stay away from exposed aluminum as it will corrode rapidly in a moist environment. I've seen aluminum cable tray in utility tunnels fall apart within 10 years. Use hot-dipped galvanized steel, stainless or non-metallic materials.
jacket: must be impervious to moisture. Don't use unjacketed C.N. cable or unjacketed CLX.
support: cable tray?
Does this help?
ofcourse this helps but I need a little more detailed information and some photos and techniques for cabling too.
Here are some photos of typical looking utiltiy tunnels-
Some general technical info on medium voltage cable application-
See this link for temperature derating factors from one cable manufacturer. Consult your manufacturer for exact numbers-
For cable tray and other support systems-
Some articles found at IEEE-
Gregory, B., Choices and considerations for the selection of power cables in tunnel installations. Cables in Tunnels (Ref. No. 2000/070), IEE Seminar , 2000 Page(s): 8/1 -8/9
Schroth, R.G.; Obst, D., Long distance tunnels for the installation of 400 kV XLPE cables. Cables in Tunnels (Ref. No. 2000/070), IEE Seminar , 2000 Page(s): 4/1 -4/4
Mendez, J.M., Sr.; Monteys, J., Design of power and communication cable installations to minimise interference in tunnels. Cables in Tunnels (Ref. No. 2000/070), IEE Seminar , 2000 Page(s): 6/1 -6/6
Anders, G.J., Rating of cables on riser poles, in trays, in tunnels and shafts-a review. Power Delivery, IEEE Transactions on, Volume: 11 Issue: 1 , Jan 1996 Page(s): 3 -11
Ohata, K.; Sakurai, S.; Ichiyanagi, N.; Shibata, K.; Inoue, T., Transient temperature rise of tunnel for power cables
Power Delivery, IEEE Transactions on , Volume: 5 Issue: 2, Apr 1990 Page(s): 745 -752
thank you alehman.
I appreciate your help.