Cjrac
Mechanical
- Sep 16, 2013
- 10
During commissioning of a new modulating 105 ton screw chiller, the chiller kept tripping due to high head pressure. It was found that the condensing unit capacity of 105 tons was matched to the chiller without taking into consideration the added heat of compression (approx. 20 tons). There was a 20% safety factor incorporated to the design, so would it be possible to de-rate the chiller 20% (without taking away from building comfort) in order to account for lack in condensing unit capacity and eliminate nuisance trips? Also, could the chiller be de-rated by adjusting the maximum compressor stage to 20% less than the previous max? Any suggestions would be greatly appreciated. Thanks.