There is a 3-bus bar system.
On bus1 there is the generator: 30MVA, cosφ=0.8. So active power = 30*0.8=24 MW. And Reactive power=18 MVAr.
On Bus3, there is the load: 15 MVA, cosφ=0.9. So active power = 15*0.9=13.5 MW, Reactive demand=15*sinφ=6.54 MVAr.
The concept of power factor has to do with the phase difference between V and I.
So this means that the generator can produce UP TO 24 MW of active power, and 18 MVAr of reactive power?
On bus1 there is the generator: 30MVA, cosφ=0.8. So active power = 30*0.8=24 MW. And Reactive power=18 MVAr.
On Bus3, there is the load: 15 MVA, cosφ=0.9. So active power = 15*0.9=13.5 MW, Reactive demand=15*sinφ=6.54 MVAr.
The concept of power factor has to do with the phase difference between V and I.
So this means that the generator can produce UP TO 24 MW of active power, and 18 MVAr of reactive power?