Once20036
Structural
- Oct 7, 2008
- 533
JAE started a thread about how to handle an unfortunate shear wall location.
I highjacked the thread a bit and started talking about the flexural detailing/stiffness of diaphragms and through it would be best to start a unique thread on the topic.
Some of the conversation is summarized below, the rest is here:
Flexural deflection of the diaphragm is proportional to the moment of inertia. SDI defines the I as the area of the chord member * the distance between the chord squared (ax^2, from mechanics of materials).
Using the perimeter angles as a chord makes sense for your geometry, but I suspect that you're actually getting very little flexural stiffness, right?
Do you provide a splice detail for these chord angles? I always call for continuous angles but never actually get them (fortunately I don't use them as chords typically, so its not a big deal).
Within the context of the above question, how do you calculate the moment of inertia for interconnected wall panels. Is it just ax^2 using the area of steel of the tension reinforcing bars in the wall panels? Seems flimsy, but viable.
We might need to agree to disagree on this one, as I don't see how your sketch limits diaphragm strain at the deck edge.
Take the center of the wall, where "chord tension" is highest. The two chord wall segments closest to the center will move away from one another due to the chord tensions. There is nothing to prevent this movement, or limit the strain between these two walls except the deck. I think that where the deck is perpendicular to the edge, it will flatten out some of the corrugations. Where the deck is parallel with the edge, it seems to me that this could lead to tearing of the deck. With either option (parallel or perpendicular) I`d be concerned about durability of the roof. At this point, I think that all of our flexural equations are suspect because our strain no longer varies linearly across the length of the building. We`ll have these high strain regions (at joist between wall segments) which means that actual deflection will be significantly more than expected deflection.
In your channel analogy, it looks to me like it's three flat plates, with load transfer provided by the vertical plates. This geometry is not stable without a) the flexural capacity of the web member (which we do not have in the building, due to the lack of chords) or b) the continuity/moment connections in the corners (which we do not have in the building).
I think that a more appropriate analogy would be extending the "slots cut by a terrible person" across the entire web, to eliminate any flexural strength of the web.
If I found that channel inside an existing building somewhere I`d absolutely re-reinforce it if I were going to add *any* load to it, and would likely recommend reinforcing it even if it was outside the impact of my work.
Granted, all of this is just focusing on the flexural strength. If you were to ignore all flexural stiffness and do your work based only on the shear stiffness, is your sketch more valid? Honestly, I`m not sure and would need to loop back to that question after billing some hours.
I highjacked the thread a bit and started talking about the flexural detailing/stiffness of diaphragms and through it would be best to start a unique thread on the topic.
Some of the conversation is summarized below, the rest is here:
JAE said:JAE: We have modeled the diaphragm as a series of "horizontal beams" along the edges, so to speak, with a stiffness both in flexure and shear that attempts to mimic the deflection behavior of a metal deck diaphragm under the proposed loads.
Once20036: How do you account for chord forces, given that you're counting on the flexural stiffness?
JAE: There are perimeter steel angles (supporting roof deck on the inside face of the panels that can serve as chords.
Flexural deflection of the diaphragm is proportional to the moment of inertia. SDI defines the I as the area of the chord member * the distance between the chord squared (ax^2, from mechanics of materials).
Using the perimeter angles as a chord makes sense for your geometry, but I suspect that you're actually getting very little flexural stiffness, right?
Do you provide a splice detail for these chord angles? I always call for continuous angles but never actually get them (fortunately I don't use them as chords typically, so its not a big deal).
KootK said:KootK: In the context of this conversation, the chord could also be the wall panels themselves if the wall panels are interconnected.
Once20036: I agree with you and JAE that a perimeter angle (if continuous) could function as a chord, as could properly detailed and connected walls panels.
Within the context of the above question, how do you calculate the moment of inertia for interconnected wall panels. Is it just ax^2 using the area of steel of the tension reinforcing bars in the wall panels? Seems flimsy, but viable.
KootK said:Then the show must go on. The concept essentially just takes the deck shear around the bend and utilizes the wall panels as very stiff extensions of the "web" in our beam analogy. Most of us carry truss/beam analogy, WL^2/8 diaphragm model around with us in our heads. I think that an expanded, more nuanced definition of "chord" would be:
Any thing or assemblage of things, located anywhere in space, that sufficiently limits diaphragm strain at the deck edge.
Of course, the more complicated one makes the load path, the more work it takes to demonstrate sufficiently restrained deck strain. For most building morphologies, it's not worth the effort.
We might need to agree to disagree on this one, as I don't see how your sketch limits diaphragm strain at the deck edge.
Take the center of the wall, where "chord tension" is highest. The two chord wall segments closest to the center will move away from one another due to the chord tensions. There is nothing to prevent this movement, or limit the strain between these two walls except the deck. I think that where the deck is perpendicular to the edge, it will flatten out some of the corrugations. Where the deck is parallel with the edge, it seems to me that this could lead to tearing of the deck. With either option (parallel or perpendicular) I`d be concerned about durability of the roof. At this point, I think that all of our flexural equations are suspect because our strain no longer varies linearly across the length of the building. We`ll have these high strain regions (at joist between wall segments) which means that actual deflection will be significantly more than expected deflection.
In your channel analogy, it looks to me like it's three flat plates, with load transfer provided by the vertical plates. This geometry is not stable without a) the flexural capacity of the web member (which we do not have in the building, due to the lack of chords) or b) the continuity/moment connections in the corners (which we do not have in the building).
I think that a more appropriate analogy would be extending the "slots cut by a terrible person" across the entire web, to eliminate any flexural strength of the web.
If I found that channel inside an existing building somewhere I`d absolutely re-reinforce it if I were going to add *any* load to it, and would likely recommend reinforcing it even if it was outside the impact of my work.
Granted, all of this is just focusing on the flexural strength. If you were to ignore all flexural stiffness and do your work based only on the shear stiffness, is your sketch more valid? Honestly, I`m not sure and would need to loop back to that question after billing some hours.