Just as a point of reference, there are three distinct parts that form the means of egress. You can of course look up the official definitions, but this is my layman's version of them:
1. Exit access - all spaces between you and the rated stairwell or exterior door aka the "exit". Spaces that are not normally occupied do not form part of the exit access, at least per NFPA 101.
2. The exit - the point where you enter a space that provides a protected from fire/smoke means through which you will eventually reach a public way. The exit can be a rated stairwell, a rated horizontal exit (corridor), an exterior door, etc.
3. The "exit discharge" - after leaving the exit, the exit discharge is between you and the public way. This is for example an open street or space of sufficient distance that you would go to and avoid fire exposure after escaping the building.
What you are talking about occurs in the exit access portion of the means of egress.
The level of exit discharge is the floor (basement, 1st floor, 2nd floor etc) of the exit. Therefore the level of exit discharge is unrelated to the levelness of your exit discharge.
Incidentally, I am sure IBC is the applicable code, but NFPA 101 section 7.1.6.2 does provide some intellectually interesting language if you are interested in such things. It allows abrupt changes in elevation up to 1/4" (6.3 mm) with no bevel, and allows abrupt changes greater than 1/4" (6.3mm) but less than 1/2" (12.6mm) if the edge is beveled with a slope of 1:2. Anything over 1/2" shall be considered a ramp.
Hope this helps