Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

user dauwerda 1

Status
Not open for further replies.

chuckd83

Electrical
Oct 2, 2014
42
I'm sorry, I can't seem to find a way to private message someone and the thread they posted on is closed.

dauwerda,

You posted a spreadsheet calculator on the below thread for the deratings of bundled conductors. I extracted the equations from the spreadsheet, but can't seem to find them in the cited IEEE 738 standard.
 
Replies continue below

Recommended for you

chuckd83, the "normal" ratings of the conductors are determined from IEEE 738.
The derating due to the proximity effect is put together based on the following sources (links take you to the document on IEEE website):
Skin Effect and Proximity Effect in Tubular Conductors
Skin Effect in Tubular and Flat Conductors
Bessel Functions for A-C Problems

Here is the general outline of how the calculations in the spreadsheet are set up:
conductor_proximity_effect_tq3zse.jpg
 
Thanks. Those are the equations I extracted. I took it from your post back in January that they were taken from IEEE 738. Thanks for the sources.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor