Dumbo2929
Electrical
- May 31, 2005
- 109
I have a customer with 480Y/277V transformer secondary and has installed Form 35S meter with 2CT's and no PT's. Meter is Elster A3 solid-state. The equipment end use is a PV inverter which is 3-wire, but the transformer is 4-wire, so I feel this should be 9S and not 35S. In addition they grounded the Vref at the bottom of the meter socket, which I believe is incorrect. Should the voltage Vref at the bottom of the socket be connected to the phase without the CT's and not grounded? They feel it is a delta installation but I feel it is 4-wire wye. The meter is showing about 5% error to another meter. Any thoughts?