dwyer
Mechanical
- Jul 25, 2002
- 4
Hi,
I am trying to calculate the minimum wall thickness required for a check valve. I am using the formula from ASME B31.1-1995 edition, "minimum wall thickness for a staight pipe under internal pressure", Paragrah 104.1.2.
I want to verify some valve designs done in the past.
Is this the correct formula, if not please point me in the right direction.
Thanks in advance,
Dwyer
I am trying to calculate the minimum wall thickness required for a check valve. I am using the formula from ASME B31.1-1995 edition, "minimum wall thickness for a staight pipe under internal pressure", Paragrah 104.1.2.
I want to verify some valve designs done in the past.
Is this the correct formula, if not please point me in the right direction.
Thanks in advance,
Dwyer