I have a diesel truck vehicle garage and we are adding ducts over 4' wide. So I need to hire a contractor to add sprinklers under those ducts. I've been researching IBC and NFPA 13. I need to prepare bid documents for a sprinkler contractor. They will perform detailed design. But I need to show number and type of sprinkler heads. Could someone look at this and tell me I'm on the right path?
My plans would show location of sprinkler, temperature, response time, and coverage
How do I determine the Commodity and Occupancy classification?
- trucks are diesel and some occasional gasoline vehicles; there are some misc. tires stored (but it isn't a real tire storage). Most stored items are made of steel or concrete. Some steel items can be on a wooden palette. Some fluids (Diesel DEF fluid) are in plastic tanks). Nothing stored is taller than 5-6 ft.
- Based on this classification this could be Class I or Class II. Can we ignore the trucks having fuel?
Based on NFPA 13 Table 4.3.1.7.1.1. Class I or II stored would be Ordinary Hazard I
If I use standard range sprinklers and Ordinary Hazard, NFPA 13 Table 10.2.4.2.1 (b) shows me a maximum spacing of 15 ft.
- why is there no OH I or II in those tables?
If I use Extended range sprinklers, NFPA 13 Table 11.2.2.1.2 shows me up to 20 ft spacing. but also shows me smaller numbers (down to 12 ft)
- Can I just arbitrarily decide to use extended range sprinklers?
- what determines if I can use the 12 or 20 ft? The table is a bit unclear and since the standard range is 15', what is the purpose of an extended range 12'sprinkler?
- Again, why does Ordinary Hazard "I or II" not matter here?
Other than that, I plan to use Quick Response and 135°F types. There isn't a heat source nearby. Maybe a truck could park idling under the duct, though. But I don't think that would heat the area that much. Summer can be close to 100°F, so maybe i go to 175°F sprinklers. IS there any reason a higher temperature rating is forbidden?
Thanks in advance. and I already signed up for a 3-day Fire Protection design Class to learn this better. But that is in September and I need to bid this out now.
Edit: NFPA13 A.4.3.3.2 shows Automobile garages as "Ordinary Hazard II". I still don't understand why "I or II" matters since it isn't mentioned in the sprinkler tables. I assume it matters elsewhere.
My plans would show location of sprinkler, temperature, response time, and coverage
How do I determine the Commodity and Occupancy classification?
- trucks are diesel and some occasional gasoline vehicles; there are some misc. tires stored (but it isn't a real tire storage). Most stored items are made of steel or concrete. Some steel items can be on a wooden palette. Some fluids (Diesel DEF fluid) are in plastic tanks). Nothing stored is taller than 5-6 ft.
- Based on this classification this could be Class I or Class II. Can we ignore the trucks having fuel?
Based on NFPA 13 Table 4.3.1.7.1.1. Class I or II stored would be Ordinary Hazard I
If I use standard range sprinklers and Ordinary Hazard, NFPA 13 Table 10.2.4.2.1 (b) shows me a maximum spacing of 15 ft.
- why is there no OH I or II in those tables?
If I use Extended range sprinklers, NFPA 13 Table 11.2.2.1.2 shows me up to 20 ft spacing. but also shows me smaller numbers (down to 12 ft)
- Can I just arbitrarily decide to use extended range sprinklers?
- what determines if I can use the 12 or 20 ft? The table is a bit unclear and since the standard range is 15', what is the purpose of an extended range 12'sprinkler?
- Again, why does Ordinary Hazard "I or II" not matter here?
Other than that, I plan to use Quick Response and 135°F types. There isn't a heat source nearby. Maybe a truck could park idling under the duct, though. But I don't think that would heat the area that much. Summer can be close to 100°F, so maybe i go to 175°F sprinklers. IS there any reason a higher temperature rating is forbidden?
Thanks in advance. and I already signed up for a 3-day Fire Protection design Class to learn this better. But that is in September and I need to bid this out now.
Edit: NFPA13 A.4.3.3.2 shows Automobile garages as "Ordinary Hazard II". I still don't understand why "I or II" matters since it isn't mentioned in the sprinkler tables. I assume it matters elsewhere.