Everyone, thanks a million for all the thoughtful and helpful replies. I'll try and address some of the questions posed:
[ol 1]
[li]
LittleInch said:
Can you find an ultrasonic insulation thickness meter and then just measure the circumvent of the lagged pipe?
I asked around and apparently an ultrasonic insulation depth gauge/meter is not a tool we have on hand. Can you recommend any good brands or devices specifically?[/li]
[li]
1503-44 said:
What's the flow rate, temperature and pressure drop?
Flow rate is 385 GPM, temperature is around 45F, and I am unclear about which pressure drop exactly you are talking about. The chilled water piping is connected to some coils for a large AHU, and the chilled water is tapping off a district chilled water loop and from a chiller that will soon be demolished.[/li]
[li]
miningman said:
some sort of infrared thermal camera should provide adequate info to generate at least an initial estimate
Interesting idea, do you have a recommendation for a budget friendly tool that can accomplish this? Thinking out loud, I wonder if there is a device that can connect to my iPhone and capture thermal imaging.[/li]
[li]
LittleInch said:
Use a thin needle and the a piece of tape or glue to seal the hole?
Sometimes the simplest idea is the best! Unfortunately, there is a hard plastic casing surrounding the insulation, but I look around and see if a very strong needle would be able to puncture it somewhere.[/li]
[li]
1503-44 said:
MRI? X-ray? Ask the old guy? :=)
MRI? X-ray? Haha, I assume you are joking, but if you aren't, please fill me in! And trust me, my first go-to with these kinds of questions (after of course some personal digging and research) is to go ask the old guys![/li]
[li]
TBP said:
Order on of these - note that the mini one only does up to 6" pipe. The next 3 to the right all have the same scales, and will measure up to 16" pipe. Note that there are 2 scales, one one for nominal pipe diameter, and one for actual diameter. Cut a slit in the pipe insulation, measure the pipe, then tape the cut. Works like a charm, and resolves no end of arguments on the spot. They were sold as "Pocket Rockets" for decades, but I guess they thought that name wasn't "woke" enough. Anyway...
Cool! I looked into the tool you suggested and brought up to my boss, but he was concerned that if I were to cut into the pipe, (even if I were to 'tape the cut') that some exposed portion of the pipe/exposed insulation could begin to sweat, which he said, should be avoided at all costs. If anyone has personal experience of doing this and confirm/deny this that would be great! I might get one of these tools regardless, as they look fun to use.[/li]
[li]
hacksaw said:
What's the outside diameter of the piping including the insulation?
You might check some of the pipe fittings (flanged) as well. your heat exchangers will also provide some idea of the actual flow taking place if you have someone on site to run the calculations.
Chilled water systems have recommend pipe sizes based on the cooling capacity of your compressors.
The outside diameter of the pipe is 8"Ø. And I'll check the flanged pipe fittings to see if that will help. I fortunately know the flow circulating through the coils (only demand for the chilled water piping in this particular building) for the AHU. Interesting point you bring up, because the chilled water is currently being supplied by an in-house chilled but it's also supplying/leaching from district chilled water piping. So I'm not sure if the cooling capacity of the compressors (you mean cooling capacity of the chiller?) would help me in this case.[/li]
[/ol]
I apologize for the long response - I like to be thorough! Thanks again for all the help so far.