twinnell
Structural
- Jan 20, 2005
- 212
The building construction (built in 1989) is 12 inch fluted CMU bearing walls with pilasters (24"x24") at 10 feet on center. Walls are 28'-0" tall and sit on a 6 feet tall concrete foundation wall. Building dimensions are 57'-4" x 46'-8" with a 1 inch control joint at midspan of the 57'-4" wall. No control joint in the shorter wall. Wall supports roof joists at 4'-0" on center supporting metal roof deck and membrane roof. No pilaster in corner. First pilaster is approximately 8 feet from corner in both directions.
Crack starts at center of 3'-0" door lintel and stair steps over toward corner and then vertical along head joint closest to corner. The edge of door is located approximately 24 inches from the outside face of cmu. It appears that due to wall dimension, head joints for cmu at this location are approximately 2 to 4 inches apart. So the crack goes back and forth between the head joints. The crack is actually in the long wall (has control joint).
Typical wall reinforcing consists of 6-#6 pilaster reinforcing and a #6@48 from centerline of each pilaster. Which puts two bars 2'-0" apart centered between pilasters. Horizontal reinforcing is #12 wire every other course. Also, 1-#6 each side of opening and at corners. All bars centered in cells except pilasters, they are out at face.
This building is basically on the beach in outer banks of North Carolina.
No signs of settlement in the foundation wall.
Any thoughts on the cause of the crack and repair solutions? My thought was that it is due to expansion/contraction. Did not verify that reinforcing was installed per above. Since wall is primarily spanning horizontally between pilasters and corner wall, wasn't sure it that is actually the case for a vertical crack. would tuck pointing the crack be acceptable? Would it just happen again? I wouldn't think you could put a control joint at the crack location since spans horizontal and not vertical.
Any thoughts would be appreciated. Thanks.
Crack starts at center of 3'-0" door lintel and stair steps over toward corner and then vertical along head joint closest to corner. The edge of door is located approximately 24 inches from the outside face of cmu. It appears that due to wall dimension, head joints for cmu at this location are approximately 2 to 4 inches apart. So the crack goes back and forth between the head joints. The crack is actually in the long wall (has control joint).
Typical wall reinforcing consists of 6-#6 pilaster reinforcing and a #6@48 from centerline of each pilaster. Which puts two bars 2'-0" apart centered between pilasters. Horizontal reinforcing is #12 wire every other course. Also, 1-#6 each side of opening and at corners. All bars centered in cells except pilasters, they are out at face.
This building is basically on the beach in outer banks of North Carolina.
No signs of settlement in the foundation wall.
Any thoughts on the cause of the crack and repair solutions? My thought was that it is due to expansion/contraction. Did not verify that reinforcing was installed per above. Since wall is primarily spanning horizontally between pilasters and corner wall, wasn't sure it that is actually the case for a vertical crack. would tuck pointing the crack be acceptable? Would it just happen again? I wouldn't think you could put a control joint at the crack location since spans horizontal and not vertical.
Any thoughts would be appreciated. Thanks.